Bedroom window trouble
Info:
Weight of window is 26.5 lbs
throw (up/down) of window 25.5"
dual coils in balance each marked 540. coils are attached one on each side of the pivot shoe.
balance: 3"(H) x 1-1/4" (W) X 1/2" (D)
Pivot bar (U channel) same dia as your 26-089 or 26-040
Pivot shoe same diam as your 15-046 (1-1/4"(w) X 1/2" (D)
Let me know what you recommend to keep the window from closing.
Thank & waiting your response
Suspect the coils (540) in the balances are not strong enough to hold up the sash with the replacement glass. Do you have replacement coils I can use in the existing balances that will hold up a 26.5 lb sash.
Thanks & waiting your response
You don't have a 15-046 pivot shoe, you have the 15-180. This is designed specifically to work with the Series 190 spring, so that's what you want to look into.
I can see the problem right away; your current springs are only rated for 5 pounds of support each. With two on each side, that's only 20 pounds of support. Like my gut on Christmas, your window appears to have gained 6.5 pounds. That's not a big deal, though, we can easily compensate for that with a new combination of springs.
I think a better combination now would be to use one 7 pound spring and one 6 pound spring per side. That will give you 13 pounds of support on each side, for a total of 26 pounds. That should be fine, you won't miss that last half a pound.
With that in mind, I recommend an S190-740 and S190-640 coil spring. You can reuse your old shoe and clips, they should be totally compatible.